5/16/2015 12:56 AM | |
Posts: 93 Rating: (2) |
Dear Sir,
We ordered 15 Multirangers with Smartlink cards for Profibus DP communication. Products received are fine, we updated the required GSD files also, but module LED is continuously "RED" which means it is OFFLINE. We tried the parameters like:
P794 = 2 P795=1
Unfortunately, it is still showing OFFLINE. Attaching herewith picture of Multiranger (removed from site to check in workshop with PLC) and screen of Step7 software page for your review.
I think I am missing some step but not sure which one.
Thanks and looking forward to receive positive feedback.
Regards,
Davinder Singh AttachmentCASE_MULTIRANGER_r1.pdf (124 Downloads) |
5/18/2015 9:05 AM | |
Joined: 12/13/2012 Last visit: 10/5/2023 Posts: 124 Rating: (45)
|
Hello ,
Your setting 794 = 2 and 795 = 1 are o.k. Sure that the bus connection at the smartlinx card is not interchanged ?
A = 3
B = 4
Attached you will also find a guide for the configuration.
Hope this helps !
Cheers
AttachmentSmartLinx Profibus and step 7.doc (150 Downloads) |