6/29/2013 4:33 PM | |
Posts: 9 Rating: (1) |
Hello I`m a beginnerin this world of automation so my knowledge is very limited, but increasing....... I purchased a S7 1200 for testing my programs,soI have been programming for several weeks, and now, I would like to try with WinCC RT. I want to learn programming and SCADA simultaneously. I`m using Tia Portal V12 and WinCC Advanced.
I attached a pdf file that contains all the screens in the programming process from the beginning. I do not know what is happenning. I do not have any complete similarexample for comparing. AttachmentRuntime Example.zip (396 Downloads) |
6/29/2013 7:39 PM | |
Joined: 3/18/2008 Last visit: 12/8/2023 Posts: 1750 Rating: (272) |
Hello, Have you gone through this important Tip published by Ganesh.
Also, you can refer entire Link Here Getting Started WinCC V12 |
VANDE MATARAM..... |
|
6/30/2013 10:23 AM | |
Posts: 9 Rating: (1) |
Thank you very much. I knew those documents. I actually checked them before posting, but I did not find any tips for fixing my problem. Note that the task I`m trying to do is much simpler than the one shown there. Thanks again. EER |
6/30/2013 12:31 PM | |
Joined: 4/17/2012 Last visit: 8/30/2024 Posts: 474 Rating: (10) |
Hi pls check here you will get the tag columns... if u click there you will get a list box there you have to select PLC connection or internal connection. external connection means from where you going to connect i.e PLC tag address that is called external connection
|
6/30/2013 7:12 PM | |
Posts: 9 Rating: (1) |
Maybe It was product of my ignorance. I thought I could do that way. I want the runtime to read the status of the bits I0.0 and Q0.5, in the program block Main OB1 that are bool tags. For that task I added two rectangles and set the Appearance like shown in the last pages of the attached document. I`m not using IO Fields anymore but It does not work anyway. What am I doing bad? Thank you AttachmentSample 20130630.zip (366 Downloads) |
6/30/2013 9:47 PM | |
Posts: 9 Rating: (1) |
Hi
I tried and nothing.......
Thanks anyway.
EER
|
6/30/2013 9:58 PM | |
Joined: 1/28/2009 Last visit: 9/10/2024 Posts: 6849 Rating: (1365) |
Hello, Why don't you try ask your issue here (Support Request).I am sorry for the problem at my earlier post and it was because of language barrier .All snapshots was in french or other langauge that I could not find the keywords easily.Share the remedy in case of conqure! Best regards Hamid Hosseini |
6/30/2013 10:22 PM | |
Posts: 9 Rating: (1) |
It is a great idea hdhosseini I am following your advice about the support request. The language of the snapshots is Spanish. I changed theTIA PortalUser Interface Language to English when I noticed it. Thank you very much for your nice answers. I will post the solution to the problem when I have one. Thanks again. EER |
This contribution was helpful to1 thankful Users |
7/10/2013 7:17 PM | |
Posts: 9 Rating: (1) |
Hi, Hammid, finally, the solution for the problem was found: I created two new tags and linked them to the animations. The new tags used for the animations are now linked to the Connection_1 that is a direct Connection to the PLC. The error was using tags linked to the HMI_connection_1 The weird thing about all this, is that they were not bad configured, at least in the theory, because those tags were linked to the PLC. Thanks and best regards EER AttachmentScreens.pdf (373 Downloads) |
This contribution was helpful to2 thankful Users |