Hi Forum members,
"I am new to the forum and also a beginner with Logo. I am working on a project to create a heater/cooler system using Logo and Logo TDE. Users want to set a temperature from -20 to +30 degrees. For example, if I want -10 degrees, the cooler should run until that temperature is reached. If they want 20 degrees, then the heater should turn on. I have progressed to the point where the heater can work My issue now is that I cannot set my setpoint below 0 degrees. In other words, I cannot input negative temperatures. Is there anyone who has a tip/solution for this? All help is welcome." Block 008 = up/down counter (setpoint wanted temperature in cooler) Block 016 = comparator between pt100 and value from block 008 Regards Michel AttachmentHaakeV1.zip (9 Downloads) |
10/12/2023 5:01 PM | |
Joined: 12/18/2014 Last visit: 12/1/2023 Posts: 31530 Rating:
|
Try this ... AttachmentHaakeV2.zip (21 Downloads) |
10/12/2023 6:15 PM | |
Joined: 10/7/2023 Last visit: 11/17/2023 Posts: 7 Rating:
|
Hi, this works perfect. Thanks for the verry fast answer! Michel |