1/25/2016 1:37 PM | |
Posts: 9 Rating: (0) |
Hello!
Motor: 630A 330V
------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 1/25/2016 3:48:41 PMNew subject after splitting |
|
1/25/2016 3:25 PM | |
Joined: 9/16/2013 Last visit: 11/12/2024 Posts: 201 Rating: (23) |
hej, F60010 does not exactly say "Fuse blown", actually it says: "Armature circuit uneven current Distribution". The F60010 Error-Message also delievers also some Parameters for Fault analysis. According to List Manual:
If there is a SD-Card in your DCM, you could save some internal Error-Data on it. Please refer to: 10.33.1 Diagnostic memory from operating instructions: https://support.industry.siemens.com/cs/de/en/view/109478240 after that you can send this data to siemens Support. |
1/26/2016 4:58 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (878) |
Hello, Please check the value in r0949 which will be help to analyse the problem. HTH |
4/21/2016 6:54 AM | |
Posts: 9 Rating: (0) |
Please tell me what is MLFB nuber. Tinordi György |
4/21/2016 7:00 AM | |
Joined: 8/25/2006 Last visit: 11/13/2024 Posts: 2211 Rating: (280) |
Hello. MLFB is complete order number, e.g. 6RA8087-6DV62-0AA0. |
4/21/2016 7:04 AM | |
Posts: 9 Rating: (0) |
Motor data: Un= 220V (330V) DC In=630A If=11 A Uf= approx 220Vdc P=125 kW type: P133-6K russian (soviet) (made at 1960) n= 400/1500 (220V); 600/1500 (330V) |
4/21/2016 7:08 AM | |
Posts: 9 Rating: (0) |
MLFB : 6RA8087-6DV62-0AA0 parameter later after site inspection |