12/6/2017 3:41 AM | |
Joined: 12/18/2014 Last visit: 4/25/2024 Posts: 32884 Rating: (4066)
|
In attachment a possible solution.
AttachmentTemp_control_(0BA8.Standard).zip (232 Downloads) |
12/7/2017 6:26 AM | |
Posts: 22 Rating: (1) |
Thanks it seams that this is working like I wanted... |
This contribution was helpful to1 thankful Users |
12/8/2017 5:02 AM | |
Joined: 12/18/2014 Last visit: 4/25/2024 Posts: 32884 Rating: (4066)
|
No, you do not need an extra PT100. If you want to use several switching thresholds with the same measured temperature, you can program several threshold triggers parallel. AttachmentTemp_control_V2_(0BA8.Standard).zip (199 Downloads) |
This contribution was helpful to1 thankful Users |
12/9/2017 8:36 AM | |
Joined: 12/18/2014 Last visit: 4/25/2024 Posts: 32884 Rating: (4066)
|
At every time..... |
12/10/2017 5:33 AM | |
Joined: 12/18/2014 Last visit: 4/25/2024 Posts: 32884 Rating: (4066)
|
Why ask you twice? |
12/10/2017 5:55 AM | |
Joined: 12/18/2014 Last visit: 4/25/2024 Posts: 32884 Rating: (4066)
|
Do you even know how the web server of the LOGO! is working? How do you enable and call the web server on LOGO! 8? For each message text, which the web server should show you, you have to activate the message in the message text. |
12/10/2017 8:31 AM | |
Posts: 22 Rating: (1) |
I get it to work now. I missed that must be in run mode.. Sorry I missed that.. |
12/11/2017 9:35 AM | |
Joined: 6/19/2017 Last visit: 4/25/2024 Posts: 7958 Rating: (162) |
New question published by Theice is split to a separate thread with the subject Want to put a Summer/Winter switch that disable Q3 in Winter mode and enable in Summer mode. Best regards |