5/20/2012 6:52 PM | |
Posts: 12 Rating: (1) |
OK, here's some more information on the status lights: RN-off ST-on QVZ-on ZYK-off BASP-on Thank you in advance once again. |
5/20/2012 8:10 PM | |
Posts: 12 Rating: (1) |
OK, I checked the voltage and I'm getting 32 VDC. Is the voltage too high and it burned out the card maybe? |
5/20/2012 10:54 PM | |
Joined: 7/18/2011 Last visit: 10/9/2023 Posts: 521 Rating: (90) |
Hi bmason1623, You can find info about necessary cable here The program is in eprom, and since you performed an overal reset the PLC should read its program from the EPROM Some things you can do: Tighten all screws from all modules (CPU, output cards) Switch the PLC once from run to stop and back to run What's connected to the special CP cards? Kind regards, BV |
5/21/2012 4:18 AM | |
Posts: 12 Rating: (1) |
would a dead battery cause the BASP to go on and stop the CPU from loading? |
5/21/2012 4:59 AM | |
Posts: 1064 Rating: (72) |
basp is outputs disabled so no i don't think a dead battery would do that |