7/22/2009 4:25 AM | |
Joined: 5/18/2006 Last visit: 10/21/2020 Posts: 170 Rating: (64) |
I believe you are looking for a circuit to ensure the motor gets the appropriate cooling from the high inrush current after a start. Either via running for a continuous 60 min or staying off a minumim of 30 min. See attached. Note, in the screen shot I used 60 and 30 sec instead of minutes (makes testing more reasonable). Just change the timer-p time inputs to 3600 and 1800 secs. Note TIMER_P set for Extened Pulse mode of operation (MODE = 1). AttachmentMotor Cooldown CFC.pdf (149 Downloads) |
7/28/2009 6:39 AM | |
Posts: 24 Rating: (0) |
Hi, Carbreytj Good morning Excellent, I understand your point. Thanks and Regards, |