4/29/2015 8:14 PM | |
Posts: 93 Rating:
|
Hi all, I have two S7 400 plc. i need to combined both plc in net pro.now both plc in separte net pro configuration. so i create new file,copy and paste both cpu in single netpro program.when compiling time PLC-1 error alarm popup.But PLC-2 not pop up any alarm. Then i check PLC-1 separately compiling time same alarm popup.And showing ERROR: CPU416-2DP: 0001 A050: no local cp WARNING: Configuration on the profibus subnet (profibus2) has changed.The specified constant bus cycle time should be checked. once again i say simply both plc copy,past in a single net pro program.it's correcet or wrong.otherways i need to configure new cpu in a net pro using export function.pls go through my attachment and guide me solve the problem. Advance Thanks&Regards, Suryamuni AttachmentLINE-1 NET PRO CONFIGURATION.pptx (414 Downloads) |
5/4/2015 9:22 AM | |
Posts: 93 Rating:
|
Hi moPS04, Thanks for your reply.I checked ISO on TCP connection found both PLC i mentioned same local id.now i changed the local id on PLC-1.After compile my project no error.Thanks for your support.here my attached the photo after compile my project. Now my issue is solved. Thanks&Regards, Suryamuni. AttachmentNO ERROR AFTER COMPILE.pptx (339 Downloads) |
This contribution was helpful to
1 thankful Users |