5/20/2021 1:03 AM | |
Joined: 7/25/2017 Last visit: 9/19/2024 Posts: 317 Rating: (47) |
We have an old D445 running Simotion Scout 4.3 and Simotion FW 3.2. It controls MM440s over Profibus (12MBaud). I am looking into replacing the MM440s with G120C DPs. Integrated support of current model G120C DPs is not possible with Scout 4.3. I was hoping to use a GSD device and configure the drives externally to the Scout project. I have attached my procedure. Is it correct? Save & Compile All doesn't produce any errors. AttachmentMM440 to G120C DP in Scout 4.3.docx (696 Downloads) |
5/20/2021 6:04 AM | |
Joined: 5/12/2006 Last visit: 9/20/2024 Posts: 22365 Rating: (3011)
|
looks ok |
This contribution was helpful to1 thankful Users |
3/17/2022 4:14 AM | |
Joined: 7/25/2017 Last visit: 9/19/2024 Posts: 317 Rating: (47) |
I have tested and confirm that the above procedure works. Parts used:
|
Follow us on