Hello; The DB you show is part of your S7 PLC program. But the data you transfer over Profibus from the Wago Profibus scanner is exchanged using I/O addresses attributed by the HWConfig Profibus configurator and transferred by functions SFC15 and SFC 14 (to ensure consistency of the data transmission) . This you can validate from this Wago application note for their Profibus couplers, attached to a S7 PLC: http://www.wago.com/wagoweb/documentation/app_note/a1008/a100800e.pdf How are you programming the transfer of the Profibus data to your DB? Are you sure that the data transferred is actually the RS-232 data from the scanner? For example, how did you program SFC15/14 in your S7 program? Hope this helps, Daniel Chartier |