Hi Mr_Prof I think that the easiest solution is to create a screen with an "Alarm view" object and, in case the connection fails, you will be able to see an alarm as explained here: Procedure if there is no connection Hope it helps! |
Last edited by: JimHalpert at: 01/09/2025 15:07:05If this post has been useful, don't forget to rate it!😊 |
|
1/10/2025 2:09 PM | |
Joined: 4/26/2012 Last visit: 2/17/2025 Posts: 1621 Rating:
|
Hello, I saw that there is this option in V20, I haven't been able to test it yet, if you do, give us feedback here. Look in the System tags for the @ and locate the connection and "_PLC_OpState" value 8 is run PLC The status is for lost communication and PLC in stop. Good luck.
AttachmentVideo_1736521452.wmv (14 Downloads) |
Last edited by: rdoliveira at: 01/10/2025 14:09:35edit Last edited by: rdoliveira at: 01/10/2025 17:13:36edit Last edited by: rdoliveira at: 01/10/2025 18:06:05video Last edited by: rdoliveira at: 01/10/2025 18:20:25edit "Always make a backup before and check the best time before testing." |
|