2/9/2009 1:58 PM | |
Joined: 3/21/2006 Last visit: 1/14/2025 Posts: 10239 Rating: (1182) |
Hello eqbal, About CP5611settings look at How do you configure a PC station as DP master for connecting to a DP slave for the SIMATIC NET OPC server with the SIMATIC NET PC software? Now the question if this non siemens can be assign like Profibus Slave. In your case did Mitsubishi PLC FX Profibus slave? I found this in net PROFIBUS DP PLC Slave Interface -
Did this modul useful for your type PLC? Or your PLC supports only Profibus Master? Better contact with manufacture of PLC for more details about supports of Profibus connecion. And if you give us more details about Mitsubishi PLC side, I believe that you'll receive more answers. regards |
This contribution was helpful to1 thankful Users |
2/10/2009 8:57 AM | |
Posts: 7 Rating: (0) |
Hi Umencho, Thanks for the reply, I will come back with more details. Regards, Eqbal |
2/12/2009 11:56 AM | |
Joined: 3/21/2006 Last visit: 1/14/2025 Posts: 10239 Rating: (1182) |
Hello So, for FXON-32NT-DP you need GSD file.You can download from http://www.procentec.com/gsd/profibus/gsd-files/Melcf032.gsd. Here you can find way to insall this GSD in hardware catalog in Simaic Manager. Assign how many data you'll exchange with Profibus Master. But for other type A2 are you sure for this Nr. AJ71PB93D of DPcard. I can't find any info for this into Net. But if you mean AJ71PB92D, (With the AJ71PB92D the PLC-Series AnN/AnA/QnA from Mitsubishi can be connected to PROFIBUS DP as a master module. The fast cycle time of the CPU of up to 0,15 µs/binary instruction guarantees very short reaction times also in complex control systems. Due to integrated diagnostic tools, the user will have best support during the installation of his application.). This is not useful for this application. regards |
Follow us on