10/29/2015 8:58 AM | |
Joined: 5/20/2015 Last visit: 11/6/2023 Posts: 210 Rating:
|
PG/PC DIAGNOS IS OKAY |
Let's do it... |
|
10/29/2015 8:59 AM | |
Joined: 5/20/2015 Last visit: 11/6/2023 Posts: 210 Rating:
|
SELECTED PG/PC INTERFACE |
Let's do it... |
|
10/29/2015 9:00 AM | |
Joined: 5/20/2015 Last visit: 11/6/2023 Posts: 210 Rating:
|
GETTING PING |
Let's do it... |
|
10/29/2015 9:01 AM | |
Joined: 5/20/2015 Last visit: 11/6/2023 Posts: 210 Rating:
|
WINCC CONNECTION SETTING IN TAG MAMAGMENT |
Let's do it... |
|
10/29/2015 9:03 AM | |
Joined: 5/20/2015 Last visit: 11/6/2023 Posts: 210 Rating:
|
TCP/IP SETTING IN WINCC |
Let's do it... |
|
10/29/2015 9:46 AM | |
Joined: 4/24/2006 Last visit: 12/1/2023 Posts: 8596 Rating:
|
Hello gabbar, Have you seen this link: WinCC Connection to S7-1500, S71200 and ET 200SP Perhaps it is useful. Are you using a S7-1200 fw4 or higher? From CPU firmware V4 you have to activate the connection mechanism "Permit access with PUT/GET communication from remote partner (PLC, HMI, OPC, ...)" in the PLC properties in the menu "Protection". Best regards, Wizard |
10/29/2015 1:09 PM | |
Joined: 5/20/2015 Last visit: 11/6/2023 Posts: 210 Rating:
|
THANK YOU DEAR... |
Let's do it... |
|