How many connections does that s7-1200 have? HMI, drives, profinet devices, remote I/O? I have to wonder if you are hitting a profinet limitation. To test that theory, you could disconnect an HMI and see. To get a better answer, you can of course send your question to Support Request |
science guy |
|
1/16/2014 3:12 PM | |
Posts: 10 Rating:
|
Hi did you try huggy's idea? please resert the PLC to factory default and dowload again...... let us know. |