1/8/2015 6:13 PM | |||||
Posts: 31 Rating: (0) |
Hi all, I have a S7-1200 with a RTD module which wire break diagnostic enabled. I want to use OB82 to detect which channel is in error and what is the error. I didn't found how to detect these signal: - incomming or outgoing event - error type i.e.
SignalI'm looking for are similar to OB86_EV_CLASS and OB86_FLD_ID in OB86. I already read this note but there is no explanation on what I need: http://support.automation.siemens.com/WW/llisapi.dll/42781105?func=ll&objId=42781061&objAction=csView&ClusterID=42261900&foldersopen0=%2D227%2D226%2D175%2D174%2D173%2D251%2D&nodeid0=41885258&lang=en&siteid=cseus&aktprim=0&extranet=standard&viewreg=WW&load=treecontent&start=%2711%27&csSort=%2DDOCDATUMBEITRAG&subtype=130000 |
||||
6/15/2015 1:46 PM | |
Joined: 11/29/2011 Last visit: 4/24/2024 Posts: 1354 Rating: (229) |
Hi, Maybe this link help you: Which organization blocks do you need for error handling in STEP 7 V5.5? About understanding the diagnostic data, you might find useful the System Software for S7-300/400 System and Standard Functions Volume 1 and Volume 2 (dated to 2010 but I did not find any newer then that). Regarding to OB82 see chapter "1.18 Diagnostic Interrupt Organization Block (OB82)". There is a table detail the variables in the OB local data. |
Last edited by: MicroMan at: 6/15/2015 1:56:49 PM- What you read here, please check with manuals and your requirements. |
|
This contribution was helpful to2 thankful Users |