6/25/2013 9:21 AM | |
Joined: 2/6/2009 Last visit: 9/1/2025 Posts: 940 Rating:
|
Hi, Mr.hdhosseiniis right, The OB 81 executes only when the error comes newly. It won't execute continusoly during the presence of the Error. Try to clear the error and recreated it, this time your logic should be executed
|
_______________________________________________________________ |
|
6/25/2013 10:52 AM | |
Posts: 1064 Rating:
|
did you clear the fault so that the eroor would be retriggered? |
6/25/2013 10:55 AM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
And there is a BATTF on my power supply card. In that case M 81.0 should be "SET", untill I "RESET" it. It is not happening. ????? Hello, Check the point here: Battery error with the S7-400: OB81 is not called
do you use S7 400H? Best regards Hamid Hosseini |
6/25/2013 11:01 AM | |
Posts: 1064 Rating:
|
As Saravana told you earlier you need to clear the fault then retrigger it to test your logic |
6/25/2013 11:31 AM | |
Posts: 1064 Rating:
|
turn off the battery check switch wait a few seconds and turn it back on it should call ob 81 and run your code |
6/25/2013 11:39 AM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
Hello, Besides what mentioned, I suggest reading section related to "Operator controls and indicators " of THIS manual because "comments from experts never substitue reading manuals"! 3.1 Common characteristics of the power supply modules 3.3 Backup battery (option) 3.4 Operator controls and indicators 3.5 Fault/Error messages via LEDs Best regards Hamid Hosseini |
Last edited by: hdhosseini at: 6/25/2013 11:44 AMLast edited by: hdhosseini at: 6/25/2013 11:41 AM |
|
This contribution was helpful to
1 thankful Users |
6/25/2013 12:22 PM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
Hello, check the following topics on similar issue: S7 400H LED Status Display Problem 400H LED Status Error How do you read out the operating state and status of an H system? and
Hope that helps Hamid Hosseini |