Hello, Can you please provide us some screenshots or PDF printouts of the program in OB82. The problem is the fault OB's only run for one cycle (at incoming and outgoing Fault) so you have to store the information in another FC or FB to transfer it to Screen or whatever. Attached an example with OB86 it stores the information in MB those bytes you use elswhere in your progam to get the staus off the stations Regards, Marcjan AttachmentOB86.pdf (76 Downloads) |
Last edited by: Marcjan at: 4/18/2012 9:36 AMProblem solved? |
|
4/18/2012 9:43 AM | |
Joined: 1/28/2009 Last visit: 6/6/2023 Posts: 6804 Rating:
|
Hello , For more details on how can you implement such thing , and technical data on mentioned OBs please refer to chapter 1 of the following manual: http://support.automation.siemens.com/WW/view/en/44240604 List of all SFCs and SFBs related to diagnostics and handling PROFINET functions also included. Also check the following link ,How start information of OB86 and SFC51 used to diagnose PB slave failure. I wanna know when DP Slave has a failure - OB86 Best regards, Hamid Hosseini |