2/14/2016 8:06 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Hello, Have you checked the status of internal/control word in r0898. Bit 0 should be 0 & bits 1,2,3,4,5,6 must be 1. Please check the status when applying OFF1. How much is the value in P1122? Please refer r0046 (sheet attached here with for ready reference). OFF1, OFF2, OFF3, RFG signal status msut follow as per the signals mentioned. HTH. AttachmentOFF1 problem .pdf (129 Downloads) |
Last edited by: PISCEAN 2010 at: 2/14/2016 8:27:32 AMr0046 sheet attached for more information. |
|
This contribution was helpful to2 thankful Users |
2/14/2016 2:08 PM | |
Joined: 5/22/2012 Last visit: 3/24/2022 Posts: 895 Rating: (67) |
What is p1082 and what was your speed setpoint? |