9/4/2019 5:14 PM | |
Joined: 8/1/2012 Last visit: 11/13/2024 Posts: 76 Rating:
|
Hi. Anyone here has done projects using OLM/G12-1300? This is the current architecture - OLM Architecture I'm experiencing an issue which I can't say if right or wrong. I managed to get the redundancy working for the 2sets of IM153 (see attached pdf). But if I turn off an OLM at the PLC side, I cant get the communication to work, OLM CH2 or CH3 LED (depends of course which channel I used) keeps on blinking orange means no connection to partner. I have to plug in and out the profibus connector a lot of times until I get a solid orange at OLM CH2 or CH3 LED. My success rate in getting the redundancy working is 1 out of 10. (see this vid - OLM2 Another weird thing is, let's say redundancy works, In the SCADA I kept getting an alarm about slaveXX loss of redundancy every after few seconds (see attached pic and this vid - OLM1) Regards, wantutri |
Last edited by: wantutri at: 09/04/2019 17:15:09 |
|
9/10/2019 1:27 PM | |
Joined: 8/3/2009 Last visit: 3/19/2025 Posts: 15032 Rating:
|
Hello i Think there are still Problems in WinCC redundancy. Which WinCC Version do you use? -> check all your WinCC Systems with the Following FAQ: LINK And shutdown the Standby Server . And then restart again, do you still get the Messages? Check also the @redundant Tags if they have valid combinations. Check the Diagnose Folder of WinCC. Bye Murof |
If this Information really helps, you could use the Rate function |
|