2/14/2012 1:50 PM | |
Joined: 10/26/2011 Last visit: 1/23/2025 Posts: 762 Rating:
|
If the Q0 is interconnected to an IN_OUT (such as a reset on an Interlok) then the Q0 will be overwritten by the RESET command. Solution Place an OR block between the RESET and the Q0. This behavior is documented in SCL Help File. Declaration of Local Variables and Parameters --> Local Variables and Block Parameters. Look for the section "In/out parameters". Additional Information Please see also: http://support.automation.siemens.com/WW/view/de/16649959 |