Hi all, i would like to know which cable I should use to communicate OP7 with S7-200 plc .Also I would like to know which cable i should use to download configuration from pc to OP7. Regards Demies |
8/31/2005 4:03 PM | |
Joined: 8/10/2005 Last visit: 4/9/2024 Posts: 1486 Rating:
|
Dear Sir, Which cable I should use to communicate OP7 with S7-200 plc >>> MPI cable with ordering number 6es7901-0bf00-0aa0 Which cable i should use to download configuration from pc to OP7 >>> PG/PC cable with ordering number 6xv1440-2kh32 Best regards Your Technical Support for Automation & Drives SIEMENS AG |