1/31/2012 7:36 PM | |
Joined: 1/26/2007 Last visit: 3/8/2025 Posts: 123 Rating:
|
hello , i was doing an OS update to an op 77A using Cpu 315 2 Dp and mpi usb adapter (i do not have ppi cable ).Os update isneeded to be able to transfer new project on. he transfere all datas , 3 from 3 , and he erase flash memory data Prosave give me an error transfera data failed Now when i boot , is apear : fist time OP77A boot loader 2010 07.xx and after that goes to next screen to This device contains free software , see info/Setings for details . and remain here .. please help me to fix this to go to transfer area or to initial factory setings |
2/1/2012 5:43 AM | |
Joined: 8/31/2010 Last visit: 2/8/2025 Posts: 1524 Rating:
|
Hello aliuta2000, Check this FAQ on How do you do an operating system update (OS update) on operator panels? In your case you may need either RS232/PPI Multi-master cable (6ES7 901-3CB30-0XA0) or USB/PPI Multi-master cable (6ES7 901-3DB30-0XA0) to |
Like it? Rate it! |
|
2/1/2012 8:10 AM | |
Joined: 1/26/2007 Last visit: 3/8/2025 Posts: 123 Rating:
|
I succed to have an USB-PPI Multi master cable . olso i have an CP 5711 Adapter also (is ok tu use CP 5711). i hope i will sove tonight should i mark there Booting ?? or just os update again |
Last edited by: aliuta2000 at: 2/1/2012 8:40 AM |
|
2/1/2012 9:33 AM | |
Joined: 8/31/2010 Last visit: 2/8/2025 Posts: 1524 Rating:
|
Hello aliuta2000, You need either one of the above mentioned two cables only in case ofUpdate OS and Reset to Factory Settings. You will be able to Update OS with other supported cables but not perform a Reset to Factory Settings. since USB PC adapter (6ES7972-0CB20-0XA0) supports OP77A, CP5711 should not have any issues with downloading / Updating OS. |
Like it? Rate it! |
|
2/1/2012 9:38 AM | |
Joined: 8/31/2010 Last visit: 2/8/2025 Posts: 1524 Rating:
|
You can check the option "Reset to factory settings" if the OS is not at all booting / only a blank screen is displayed. (this may happen if there's a power failure during updation of OS) If the above mentioned is not the case, you can uncheck the option and do OS update. |
Like it? Rate it! |
|
2/1/2012 7:43 PM | |
Joined: 1/26/2007 Last visit: 3/8/2025 Posts: 123 Rating:
|
Ihave got a meesage from Siemens support .They are telling me that is not supproted an Os update via Mpi / dp cable -CPU and OP , but in the OP manual is written that is working . i am toal agree with Siemens , now , but a need a procedure to get the panel from current state to normal running , and after taht to put my project on OP. |
Last edited by: aliuta2000 at: 2/6/2012 9:07 AMLast edited by: aliuta2000 at: 2/1/2012 7:44 PM |
|
2/1/2012 8:16 PM | |
Joined: 1/26/2007 Last visit: 3/8/2025 Posts: 123 Rating:
|
i succed to restore factory setings , but by pressing some key(s) . if i just let in "restore factory setings " nothing happend , but with some keys pressed (do not ask witch key cause i press them random arraows esc enter )OP start to do transfering restorey factory settings Also i have change on the back swich configure from all to line for DP/MPI/PPI to RS 422/485 . now i am doing an os update . and is in erasing flash -> copying to flash. I am using an USB-PPI multimaster cablle 6ES7 901-3DB30-0XA0 Thank you to all |
Last edited by: aliuta2000 at: 2/6/2012 9:05 AM |
|
This contribution was helpful to
2 thankful Users |
11/19/2015 2:34 PM | |
Joined: 3/2/2007 Last visit: 3/11/2025 Posts: 979 Rating:
|
it works. (no need for pressing keys on op77a) i did exactly as described in the below link. switch off the power supply for the operator panel. use usb to ppi cable, all op77a dip switch off. open prosave, select op77a and communication type. goto os update, select image file, and click reset to factory settings. click os update. power up the op77a. ... [ Resetting the Operating System to the Factory Settings (Booting) ] https://support.industry.siemens.com/cs/document/19701610/how-do-you-do-an-%22operating-system-update%22-(os-update)-or-%22reset-to-factory-settings%22-on-operator-panels?dti=0&lc=en-US |
... thank you ... |
|
11/19/2015 3:06 PM | |
Joined: 5/28/2008 Last visit: 3/12/2025 Posts: 4518 Rating:
|
Hello, To solve your problem, you have to do the folowing steps:
Hope this helps. |
Ayman Elotaify |
|
11/19/2015 3:55 PM | |
Joined: 3/2/2007 Last visit: 3/11/2025 Posts: 979 Rating:
|
thank you |
... thank you ... |
|