Hello Domloe The S71500 PLCs do not yet support OPC UA HA (Historical Access). Only OPC UA DA (Data Access) at the Moment. But you can use A WinCC Professional RT or a winCC V7.X for HA access. The SCADA Systems could do the Logging of the proicess data and offer OPC UA HA Access: https://support.industry.siemens.com/cs/de/en/view/109763315 Bye Murof |