Joined: 9/3/2008 Last visit: 1/30/2025 Posts: 932 Rating: (163) |
Hi, I think that I overlooked which type of panel you used The MP377 is a WinCE operating system. This has no COM/DCOM capabilities so it cannot communicate OPC DA. It can only work as a OPC XML Server. Take a look at: SIMATIC HMI WinCC flexible 2008 Communication Part 1 http://support.automation.siemens.com/WW/view/en/18797552 See part "4.1.2 Using the HMI device". You can install the OPC XML Gateway on the PC that connects to the MP377 and then exchange data between the two servers that way or you can use another OPC XML client directly to the panel. |
Michael |
|
12/12/2013 10:32 PM | |
Posts: 7 Rating: (0) |
I am a bit confused about your application, but have a look at these products: http://industrial.softing.com/en/products/functionality/software/opc-middleware/opc-easy-connect-suite-sw-package-to-optimize-opc-communication.html |
12/13/2013 7:43 AM | |
Joined: 3/31/2009 Last visit: 7/16/2024 Posts: 191 Rating: (3) |
you need to create the tag in wincc for specified tag on opc server |
12/13/2013 10:14 AM | |
Posts: 6 Rating: (0) |
i created a tag...but it doesn't see a value from the OPC Server.... |