Hi, for a second modbus connection, you have to create a second connection in the connection DB, e.g. ID 2. The best way to do this is with the ModbusTCP Wizard (http://support.automation.siemens.com/WW/view/en/31535566). After that you have to insert a second modbus instance (with a new instance DB for the modbus block) with the second ID. Wüstenräuber |
6/26/2009 8:53 AM | |
Posts: 28 Rating: (0) |
Thanks for the help thus far. I have attached the program. I am using instance DB 102 in OB 1 which has DB5 as the modbus parameters that was configured with the wizard and this has a connection id of 2. In OB 1 InstanceDB 103 is then used with ID 1 and a call of Modbus DB 2. I am calling the instance db's in OB 100 as well.
Attachmentmodbus.zip (853 Downloads) |
6/26/2009 10:11 AM | |
Posts: 28 Rating: (0) |
Dear Wuestenraeuber I Have made the changes you sugested but I still dont achieve comms to both devices, is there maybe another problem. Attachmentmodbus.zip (823 Downloads) |