10/24/2013 11:30 AM | |
Posts: 77 Rating: (1) |
Hello I just want to ask what do you mean by output 4xRelay/10A? per every Q1 output max is 10A or that is the whole 4 output 10A max? please advise. thanks. |
10/24/2013 11:51 AM | |
Joined: 1/21/2013 Last visit: 3/19/2024 Posts: 4618 Rating: (705) |
Hi jonjon13, 4xRelay/10A means they are 4 relays and each relay 10A max. maybe is better that look at the manual in the technical specifications: http://support.automation.siemens.com/WW/view/en/50074616 |
Last edited by: Ste39 at: 10/24/2013 12:01 PMLast edited by: Ste39 at: 10/24/2013 11:51 AM |
|
10/24/2013 12:19 PM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (713)
|
Hello, Please note that it is not 10A in all occasions, i.e. if you planned to use a 10A motor on these tiny relais, they will work only for a (verry) short time. If you have a load that is at the limit of this relay, please use external relay. Same if you have a high switching frequency. If you need more details about the relais it's Schrack V23061-A1007-A302 24v= (for 230 and 24V Logo, 12V Logo types have 12V coil), see attached Datasheet. Regards, Marcjan Attachmentrelais Logo.pdf (127 Downloads) |
Last edited by: Marcjan at: 10/24/2013 12:31 PMProblem solved? |
|
This contribution was helpful to1 thankful Users |
10/25/2013 7:51 AM | |
Posts: 77 Rating: (1) |
Thank you for the information I will use the logo unit to my spotlights... Have a nice day. |
This contribution was helpful to2 thankful Users |