Dear plcmange, parameter p0852 is called "Enable operation". If the signal is set to FALSE during operation, the drive will disable the pulses and spin out without any ramp up to standstill. If you want to use a ramp for braking please use parameter p840 (On/Off) or p848/p849 (Quick Stop). By using p840 please use the ramp function generator and configure the ramp with p1120 up to p1134. When using Quick Stop parameter p1135 - p1137 are necessary. Please find detailled informations in the operation manual of the G120P under the following link: https://support.industry.siemens.com/cs/ww/en/view/109818090 The ramp function gererator ist described in chapter 8.18.6 |