7/24/2019 8:57 AM | |
Posts: 80 Rating: (0) |
It means if one of the flow meter had a fault , with redudant system , dp/op link will stay ruñ? |
7/24/2019 4:00 PM | |
Joined: 9/27/2006 Last visit: 9/19/2024 Posts: 12282 Rating: (2684) |
Hello runaway; You have many questions, most of them should find their answers in a review of Profibus-PA (and how it differs from Profibus-DP): Start by opening the introduction to this manual from SMAR, it gives a great overview of Profibus-PA: Profibus-PA manual (SMAR) : www.smar.com/PDFs/Manuals/GERAL-PAME.pdf Next: Cable and connectors for Profibus-PA is different from the ones you use for Profibus-DP. DP uses the RS-485 standard, and PA follows the Manchester-Coded Bus-Powered standard, and the cable is different (different construction, different capacitance): PA Cable: -Siemens: :6XV1830-5FH10 (non-EX) or 6XV1830-5EH10 (EX) See the Siemens Industry Mall: https://mall.industry.siemens.com/mall/en/WW/Catalog/Products/9300219?tree=CatalogTree -Belden : 3076F (standard) https://www.belden.com/products/industrial/cable/bus-cable/profibus PA Connectors : -Siemens: see attachment below, SplitConnect system -MTL MegaBlocks https://www.mtl-inst.com/product/megablock_range_of_wiring_hubs/ Distances: a Profibus-PA segment can cover up to 1900 m, and should be terminated (both connector systems proposed have termination systems). You need a redundant IM 153-2 (for a redundant DP/PA link) only if you have 2 redundant Profibus-DP masters in your system, such as a S7-400H project. For your application (from the little information we have) it does not seem necessary. As far as diagnostics are concerned, all Profibus-PA exchanges contain exactly 5 bytes with each connected and configured instrument. The first 4 bytes hold a REAL value (IEEE floating-point format) that shows the main measurement from the instrument, The last byte is a status code that you can find in the instrument's PA manual, and that you can decode in your PLC or HMI to warn or alarm the operator. If this information is enough for your project, you need no other software. However if you also want to calibrate, change PA addresses on the instruments, otherwise modify or monitor the functioning of the instruments, you will require a software named PDM (Process Device Manager): open the Product Information tab for an overview of PDM versions. https://mall.industry.siemens.com/mall/en/WW/Catalog/Products/10023472?tree=CatalogTree Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 07/24/2019 16:08:50Last edited by: dchartier at: 07/25/2019 15:57:30 |
|
7/25/2019 2:21 PM | |
Posts: 80 Rating: (0) |
Perfect. |
10/19/2019 7:25 AM | |
Posts: 80 Rating: (0) |
dear dechartier I wonder if you could help me in the link below about this topic. regard |