Hi all; Which panel Do you suggest for communicate through AS511 on an old S5-95U PLC? Thanks in advance!
|
Regards. |
|
3/4/2014 8:04 PM | |
Posts: 8946 Rating: (999) |
You must look for a very old Panel, i.e. OP7. There is no new Simatic - panel that Support AS511. |
3/4/2014 11:14 PM | |
Joined: 8/22/2009 Last visit: 6/8/2023 Posts: 26 Rating: (0) |
Thanks IBN, is this OP7 still is for sale? |
Regards. |
|
3/5/2014 11:27 AM | |
Joined: 4/5/2006 Last visit: 8/13/2023 Posts: 642 Rating: (131) |
Hello, look for 6AV3607-1JC00-0AX1 or AX2 (OP7). Also you can look for 6AV3617-1JC00-0AX1 or AX2 (OP17). At the moment it is between Product cancellation and Product discontinuation. If you can't find one feel free to contact me. Regards André Räppel --------------------------------------------------------------------------------- www.raeppel.de
work faster withinnovative PLC-Tools |
3/5/2014 7:23 PM | |
Posts: 8946 Rating: (999) |
You will find itby a lot of resellers, also Ebay.. what country you came from? |
3/5/2014 9:21 PM | |
Joined: 8/22/2009 Last visit: 6/8/2023 Posts: 26 Rating: (0) |
Thanks to all, I'm from Mexico |
Regards. |
|
3/6/2014 7:58 AM | |
Joined: 11/21/2007 Last visit: 9/25/2024 Posts: 2325 Rating: (308) |
Hello According to the ST80 Catalog several HMI panels still support S5 AS511 ( Pl See Page 2/88 ). These include OP77B, OP177B DP, TP 177B DP, OP177B DP/PN, TP 177B DP/PN, c. You will have to use WinCC Flexible 2008 SP2 and Higher for using this protocol ( Except OP77B ) and also select Suitable convertor cable - As provided in the Catalog ( Page 2/88 ) for connecting S5-95U Programmer Port to the HMI Panels. Hope this helps Cheers Navnag |
There is no such thing as the last bug in a program |
|
This contribution was helpful to1 thankful Users |
3/7/2014 7:55 AM | |
Joined: 8/22/2009 Last visit: 6/8/2023 Posts: 26 Rating: (0) |
You are right IBN, I suggested that but the client insists on preserve your S5-95U CPUs. |
Regards. |
|
3/19/2014 3:54 PM | |
Joined: 4/5/2006 Last visit: 8/13/2023 Posts: 642 Rating: (131) |
Hello, have you found a panel? Regards André Räppel --------------------------------------------------------------------------------- www.raeppel.de
work faster withinnovative PLC-Tools |