Thank You for Your reply! I’ve done an investigation on our equipment and made the following findings; the interface-module works only without errors if it hasn’t any cards connected to its slots. I also took one of the analogue cards (that was previously connected to the interface-module) and connected it to the PLC’s rack, to confirm that there weren’t any errors with the cards themselves (which there weren’t). I also did vice versa and took one of our digital cards that was connected to the PLC:s rack and connected it to the interface-module instead. This triggered the same error that had previously occurred with the analogue cards. AttachmentPictures.zip (308 Downloads) |
Last edited by: Min_Moderator at: 10/19/2016 11:58:21 AMAdd attachment |
|
This contribution was helpful to
1 thankful Users |
1/26/2022 3:58 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
|
hi deborzanka, the error that was shown, means that the projected HW doesn´t match the real HW. When you are sure that the HW you projected is correct, this is maybe really a corrupt project. Then this behaviour could also be solved by deleting the IM-folder, like shown in this FAQ: How do you delete the IM folder of your TIA project?hope this helps, regards, |