4/6/2020 10:59 AM | |
Posts: 36 Rating: (0) |
Hi! I have the same parameter problem. I use ET 200SP CPU 1512SP F-1 PN in a TIAPortal v15.1. I only wanted to connect to the PLC and write and test some sample projects. But after I added the PLC + moduls an error occured, the DQ modules show a parameter error (flashing red LED). The PLC error LED is flashing as well. Here is some photo of the project and the set up. /I am really new in 1500 models, only used 1214 before. So I am not experienced in configurating these./ Thank you! hajleh12 ------------------------------------------------------------------------------------------ AttachmentS7-1500 ET 200SP.zip (179 Downloads) |
Last edited by: hajleh12 at: 04/06/2020 11:01:00Last edited by: Jen_Moderator at: 04/06/2020 13:52:53New subject after splitting |
|
4/6/2020 12:16 PM | |
Posts: 36 Rating: (0) |
Okay, here it is. Regard, Lehel |
4/6/2020 12:47 PM | |
Posts: 36 Rating: (0) |
Yes, the server module is there at slot 10 and working. (not showing any error msgs) Attached the pictures. Regards, Lehel AttachmentServer_Module.zip (187 Downloads) |
4/6/2020 1:23 PM | |
Posts: 36 Rating: (0) |
Hello Hati! Here are the errors what I got. (3 errors) Regards, Lehel AttachmentDQ_diagstat.zip (169 Downloads) |
4/6/2020 1:39 PM | |
Joined: 5/12/2006 Last visit: 9/18/2024 Posts: 22364 Rating: (3011) |
have you checked the baseunitis? the message say that you mounted a different baseunit color. |
4/6/2020 2:56 PM | |
Posts: 36 Rating: (0) |
And after the swap. |
4/6/2020 3:03 PM | |
Joined: 5/12/2006 Last visit: 9/18/2024 Posts: 22364 Rating: (3011) |
Hello, the 0DA0 open a new potential group the 0BA0 us the potential from the left mounted module Regards Christoph |
4/6/2020 3:06 PM | |
Posts: 36 Rating: (0) |
I replaced those 2 base units and here is the final result. Thank you Christoph! Regards, Lehel |
4/6/2020 5:52 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054)
|
hi hajleh12, following manual may help you to understand and to plan the ET200SP-system SIMATIC ET 200SP Distributed I/O systemFor example, chapter 4.1, "selecting BaseUnits" or chapter 4.5 "forming potential groups" hope this helps, regards, |
FCK WAR! |
|