10/2/2020 12:13 PM | |
Joined: 10/11/2006 Last visit: 1/22/2025 Posts: 5985 Rating: (824)
|
Hello, the speed setpoint is transferred as a percentage value referred to p2000 and following parameters. So the easiest way would be to do the conversion on PLC side an provide the adequate setpoint in percent to the SINAMICS. Please see chapter 6.6.2 of the fieldbus manual for more details. https://support.industry.siemens.com/cs/ww/en/view/109757336 |