3/27/2017 7:43 PM | |
Joined: 12/9/2010 Last visit: 10/8/2022 Posts: 623 Rating:
|
Hi Kbv, You should do connections which u have mentioned in netpro. It will be as follws- 1. Connect cpu-a to switch -1. 2. Connect cpu-b to switch -2. 3. Connect both switches to PC. 4. Interconnect both switches. Second port of cpu must be used if and only if there is ring topology. |
If you like the comment, rate it (right top) or thank it (left bottom). |
|
3/28/2017 8:45 AM | |
Joined: 6/14/2006 Last visit: 2/20/2025 Posts: 301 Rating:
|
Hi Kbv, teaming is not supported for the planmt bus connection to your PLC. You have to connect the devices like Sachinpatke mentioned. An improvement to this solution is to build a "mini" ring of your two switches: One has to be set to be ring manager. Then you need redconnect software and license. So you can set up a fault tolerant connection in Netpro. The switching of both connection is then maintained by redconnect. Have a look here to learn more: https://support.industry.siemens.com/cs/de/de/view/109476178/en Regards |