Thanks for Reply ...!!! How to Backup PCL and NC Data from Machine ? Thanks, |
4/2/2012 8:57 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello, You need to have RS232 cable. Please refer the attachement for pin connection. On PG Simocom U must be loaded. Then connect PG with RS 232 cable to simodrive & start Simocom U. You will see window (please refer the attachement). here select the option as serach for on line drive. It will automatically detects & displays On line drive. Hope this shall help you. Good luck. ![]() DEEP. AttachmentSimodrive_cable_connection.pdf (160 Downloads) |
4/2/2012 8:58 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
here is another one |
4/2/2012 9:02 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Please see attacement. Courtsy :- Siemens & Siemens experts AttachmentData_Loading_through_WINPCIN.pdf[1].pdf (159 Downloads) |
4/2/2012 9:14 AM | |
Posts: 3 Rating:
|
Thanks a Lot ...!!!! |
4/2/2012 9:21 AM | |
Posts: 2964 Rating:
|
Hello..... Check this infromation too....may be useful.... Regards, Prakash Attachment802D manual.pdf (141 Downloads) |