11/18/2016 1:37 PM | |
Posts: 67 Rating:
|
Hello all, I'm new on PDM software, i found one exist project using it but it have a small echo, all flow meter we get reading (flow,totalizer) except one flow meter we can read only tantalizer value, this is inside (simatic manger), but i want to trace this issue i run the PDM i see the configuration exist but the devise i need i cant connect on it throw pdm always i got this error please check the photos in the attachments, i need help i dont know where is the issue could be, give me some steps to trace the error and solve it, regards, AttachmentPDM.zip (62 Downloads) |
11/24/2016 4:30 PM | |
Joined: 3/28/2010 Last visit: 9/18/2023 Posts: 976 Rating:
|
The problem appears to be a mismatch between 'Profile revisions', as shown in picutre PDM (1) device expected = 3.1 device found = 3.0 But, I do PDM with HART communications, not Profibus, so I don't know whether the profile involves the GSD file or the EDD file that PDM uses. There's a list of communications download files here https://support.industry.siemens.com/cs/products?dtp=Download&mfn=ps&pnid=17320&lc=en-WW Maybe the one entitled "Profibus PA/DP Profile 3 GSD files for SITRANS F M MAGFLO MAG6000" has an update ? ? |