When you tried simulation, how much % current was drawn by motor? |
10/2/2014 8:41 AM | |
Posts: 31 Rating:
|
Dear Piscean The current was below the overload limit which is set at 120% of rated current. The drive did not trip by overload. Best Regards |
10/2/2014 1:44 PM | |
Posts: 31 Rating:
|
Not sure which phase was disconnected. Does it make any difference? Thanks |
10/2/2014 3:18 PM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Yes. That is why I ask to check by disconnecting either U or V motor supply phase. Please check & revert here. |