Industry Online Support
Technical Forum
6/17/2014 6:24 AM | |
Posts: 1064 Rating: (72) |
yes you can hook a 230 lamp across phase to phase with out neutral |
6/17/2014 8:43 AM | |
Posts: 31 Rating: (2) |
Hi... Thanks for the feedback. Can we gave PH to PH supply to 2 x 36W FLT Light Also....??Or for that we have to used Different Ballast / ELU / FLT...??? Attached here the WR Diagam for the same. Regards, Sariq Salim "Give Res[pect, gain Res]pect"
AttachmentWR_Ph-PH_2x36W.pdf (111 Downloads) |
6/17/2014 10:43 AM | |
Joined: 11/21/2007 Last visit: 8/12/2024 Posts: 2325 Rating: (308) |
Hello Sariq Salim Electrically you can operate the 240V AC Lamp or CFLs, you just have to connect your two phases instead of phase and neutral in the original connection ( Not the way you have marked ). However It is recommended from personnel safety point of view. One of the conductors should be earthed ( e.g. if the 240V supply is from a Control transformer, then one phase is usually earthed at the Transfromer end ). Hope this helps Cheers Navnag |
There is no such thing as the last bug in a program |
|