2/7/2011 4:00 PM | |
Joined: 1/28/2009 Last visit: 9/10/2024 Posts: 6849 Rating: (1365) |
For Derivative mode you need to set values for 2 parameters: TD and TM_LAG Check the STEP7 online help for this function to how select these 2 values.
Check this link for integral properties: As illustrated below, integration value is like accumulation of some values over a period of time.The most important property of integration which used mostly in Calculus is Additivity.So every an hour save LMN_I which is saved in the corresponding DB of the function block (DB41.DBD84) in my program.So I think you need some memory area to save result of integration. If you want to get rid of old integration value, subtract an old value with a new one and save in I_ITLVAL , whenever you want , you can insert this value to active integration value by I_ITL_ON.
BR |
Last edited by: hdhosseini at: 2/7/2011 5:22 PM |
|
2/7/2011 4:48 PM | |
Joined: 1/7/2011 Last visit: 3/28/2024 Posts: 2 Rating: (0) |
Dear hdhosseini, Thank you for this tip, I'll try this asap. best regards Bastien |
This contribution was helpful to1 thankful Users |
2/8/2011 7:14 PM | |
Joined: 1/28/2009 Last visit: 9/10/2024 Posts: 6849 Rating: (1365) |
Dear bma@artelis.be Also check this link for Step response to PI controller and also to get a sense of how integration time effects the LMN value. PID CONT_C FB41And also check the attachment for step response of casual diff function.BR |