1/29/2014 8:40 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715)
|
Hello, PV_I = your process value, in your case you can use your analog input directly(0-32000) Setpoint= the value you want the inverter to put at the output of the inverter 0.0 to 1023.0. if you have selected manual control you can put a value (real between 0.0 and 1.0) at Manual_output. Output= your analog output to the inverter (0-32000) I have attached a document with the settings you have to do and a PID block call. Please note the SM0.1 at the Enable, this is needed to initialize the PID. Hope it's clear now. regards, Marcjan Attachment200_PID.pdf (389 Downloads) |
Problem solved? |
|