11/24/2014 9:30 PM | |
Joined: 1/28/2009 Last visit: 12/28/2022 Posts: 6785 Rating:
|
Hello xBigGx, There is a topic that discussed this issue in details,I suggest reading the topic and check if it helps: How can you prevent the PID Compact controller of the S7-1200 from switching off when the controller is switched off and on again and in the case of invalid process values? I hope this solves your problem, Hamid Hosseini |
This contribution was helpful to
1 thankful Users |
11/25/2014 1:24 PM | |
Joined: 1/28/2009 Last visit: 12/28/2022 Posts: 6785 Rating:
|
Hello again, Thanks for the feedback. You can try "sRet.i_Mode" variable saved in the IDB corresponding to the loop.You can check if it works via a watch table and checking the current mode pllus status/error outputs.More can be found in online manual "Parameters State and sRet.i_Mode".
Also I suggest checking: TIPS for PID (FB PID_Compact) Best regards, Hamid Hosseini |
Last edited by: hdhosseini at: 11/25/2014 1:26 PM |
|
This contribution was helpful to
1 thankful Users |