1/10/2013 11:37 AM | |
Joined: 9/23/2005 Last visit: 1/14/2025 Posts: 4392 Rating: (1463)
|
Hi Input_per unit (%, temperature, pressure, etc) is set in the PID Properties (Tool box button), directory Basic Setings; the scale is set on directory Process value settings. You get the many tips about PID at: /tf/WW/en/Posts/33957#top |
Last edited by: Pegaia at: 1/10/2013 11:38 AMDenilson Pegaia |
|
1/10/2013 12:35 PM | |
Posts: 15 Rating: (0) |
I have conversion real values to percent. I send my simple project. Is it good? Thank you
AttachmentPID.zip (255 Downloads) |
1/10/2013 4:24 PM | |
Joined: 9/23/2005 Last visit: 1/14/2025 Posts: 4392 Rating: (1463)
|
Hi, I coudn't to confere precisaly the math that you use. I suggest, however to not use integer mathematical operations. Better, convert the input to float, convert the scale, and use it. In theTIP Sample program: SCALE and UNSCALE /tf/WW/en/Posts/31698#top you can find read to use blocks to analogic conversion |
Denilson Pegaia |
|