5/31/2011 9:27 PM | |
Joined: 1/28/2009 Last visit: 2/21/2023 Posts: 6794 Rating:
|
Hello friends, This is the presentation based on the function of modular PID controller from SIEMENS.In this post, I upload the user code for this application.Because of copyright issues I do not upload the actual codes. FB19 (PID) , FB13(LMNG_C) and FB22(ROC) Best regards Hamid Hosseini Attachmentprog.zip (273 Downloads) |
Last edited by: hdhosseini at: 6/29/2013 10:54 AMLast edited by: hdhosseini at: 6/3/2011 9:06 AMLast edited by: hdhosseini at: 5/31/2011 9:48 PM |
|
6/3/2011 9:54 PM | |
Joined: 1/28/2009 Last visit: 2/21/2023 Posts: 6794 Rating:
|
In this section I want to show the severe effect of power failure on loop which is still in auto mode after power return.Normally, while power recovers, we set the loop in manual. If operation requires the valve be fail to close, zero send to analog output and if the operation requires the valve be fail to open,100 send to analog output. AttachmentBigjmp.zip (183 Downloads) |
Last edited by: hdhosseini at: 6/29/2013 10:56 AM |
|
6/3/2011 10:21 PM | |
Joined: 1/28/2009 Last visit: 2/21/2023 Posts: 6794 Rating:
|
The solution is provided here.There is option of activating conversion of step change ramp in OB100.This will reduce the error and then the value on the control valve will increase(or decrease) gradually as shown in the attachment. AttachmentNojmp.zip (321 Downloads) |
Last edited by: hdhosseini at: 6/29/2013 10:50 AM |
|