Hello ssamber. Network diagnostics in the S7 PLCs start with diagnostic OBs in the user program. These are used to allow the operating system of the CPU to detect errors in the running system (including network errors from standard buses such as Profibus/Profinet). The use of the error OBs and other diagnostic tools (such as SFC 51, Read SSSLID, and FB 126 (Profibus/Profinet diagnostics tool) are described in the following manual (the same tools are available for TIA Portal):
SIMATIC Programming with STEP 7 V5.5 (Ch. 23.8.1, SSL) https://support.industry.siemens.com/cs/ww/en/view/45531107 You can also have a look at the following application examples, covering Profibus and Profinet diagnostic tools, and SNMP functions:
https://support.industry.siemens.com/cs/ww/en/view/24000238
https://support.industry.siemens.com/cs/ww/en/view/6932419
https://support.industry.siemens.com/cs/ww/en/view/57249109
https://support.industry.siemens.com/cs/ww/en/view/103949062 Hope this helps, Daniel Chartier |