Hello Fritz, I did setup redundancy using this software package, and unfortunatelly the PLC crashes during start up. This is caused by function FC100 SWR_START. Looking on the outputs of FC100: RETURN_VAL is 16#8009 – according to the REDUNDANZ manual “Slave changeover lock could not be cancelled. Cause analysis by means of return value from SFC 58. Return value stored in EXT_INFO” EXT_INFO is 16#8090 Interpreting EXT_INFO 16#8090 as an error of SFC58 would mean: Specified logical address invalid: There is no assignment in SDB1/SDB2x or there is no base address. Looking on my hardware config, the base address of CP343-1 is 256, which is exactly what I put on the input LADDR of FC100. Any help would be much appreciated |