7/28/2016 8:20 PM | |
Joined: 6/3/2014 Last visit: 4/16/2025 Posts: 660 Rating:
Hello Toombs, you can use PLC UDTs in faceplates since WinCC Advanced V13 Sp1.
To create the HMI tag of the PLC UDT datatype you Need to drag&drop/copy the datatype from "PLC data types" into the "Types" folder of the project library. Afterwards you can select it like a normal datatype. |
3 thankful Users |
7/28/2016 8:39 PM | |
Posts: 91 Rating:
Maybe this was why. What I did was create a HMI data type -- then I selected the PLC data type and it automatically converted it over from the HMI data type to the PLC data type and I didn't even need to put the PLC Data type in the types under libraries. The HMI data type could then be deleted. But probably if I do this it would make it easier to configure |
7/29/2016 1:36 PM | |
Joined: 1/30/2006 Last visit: 4/23/2025 Posts: 310 Rating:
Hi Toombs You can use PLC Data Types in your HMI project. You can use them as optimized. I have made a simple projekt and I took some Screenshots. It's in the attached PDF. Hope it helps you BR. Sven AttachmentCreate Type in PLC.pdf (1807 Downloads) |
BR. Sven |
2 thankful Users |