You can do this by following way: First add S7_m_c attribute to the different names in PLC DB. You need to right click on the name (which you have given in the DB), open the properties. and in attribute tab you can add this atribute S7_m_c (note S should be in upper case and m &c should be in lower case). After adding the attribute to the addresses in the DB. close the DB then in simatic manager *right click on the DB *go to "special object properties" *select "operator control and monitoring" , a window will be opned *click on "WinCC attribute" tab * and check mark "operator control and monitoring" check the attachment to be cleared. After doing this, you have to "compile" the winCC project to get the required wincc tag in your project.
Attachmentattach.zip (454 Downloads) |