Hello, i have made a PLC program with display messages but when i try to program the PLC it says it cant program PC -> LOGO... I've attached the program [snip] Attachmentstjernetrekant + v2.zip (64 Downloads) |
Last edited by: Jen_Moderator at: 3/6/2019 8:28:00 AMRemoved link and added file as an attachment. |
|
3/5/2019 3:01 PM | |
Joined: 12/18/2014 Last visit: 12/5/2023 Posts: 31546 Rating:
|
Hello Ulrikstokk, All your message texts are incomplete. The block "message text" has an output. This output must be wired, for example, with an open clamp, as I did. This is not necessary in the simulation, but then you can not transfer a programm to the LOGO!. Attachmentstjernetrekant + v2 _V3.zip (61 Downloads) |
This contribution was helpful to
2 thankful Users |
3/5/2019 4:16 PM | |
Posts: 8 Rating:
|
Thanks! I thought it only had to be wired to an open contact in FBD :) |