Hello DanielBarbosa Yes, you can connect OP27 to S5-95U ( 8ME02 ) on PROFIBUS. The Following Manual Describes in detail the Various Communication Options for OP27 ( BEsides other HMI Panels of same generation ) SIMATIC HMI Communication for Windows-based Systems Basically, you will need the following :
In the PLC: – AG 95U/DP For each unit (operating unit or PLC): A PROFIBUS-DP bus connector Software Requirements : ProTool configuration software, from V5.1 COM PROFIBUS from V3.x Installation: Both the physical connection as well as a function block in the PLC are required for connection of the operating unit to the SIMATIC S5. The function block is supplied with ProTool/Pro. AttachmentHMI_Profibus_DP_Connection_to_SIMATIC_S5.pdf (415 Downloads) |