8/11/2015 10:01 AM | |
Posts: 57 Rating: (1) |
Hello guys, I have the same problem in a configuration that I have with 3 slaves. I would like that the PLC before it goes to start mode, despite that a slave has a problem and is turned off, the PLC goes to start mode despite that. I have an OB82 and 86 but I saw that in case that the PLC was already in RUN mode and misses a slave (for example it is turned off for some reason), it does stay in RUN mode. But if all the system is turned off (PLC as well) and we power it on, so that all the devices are turned on and one slave does not receive voltage (I test it deliberately) then the PLC stays in STOP mode... :( Could somebody suggest me what to do, to fix that? The goal is notwithstanding this problem at STARTUP that the PLC does make it and go to RUN mode. Thank you ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 8/11/2015 1:18:31 PMNew subject after splitting |
|
8/11/2015 2:04 PM | |
Posts: 8946 Rating: (999) |
Check CPU setting in HW-config "start if actual configuration differs" (or something like that) |
8/11/2015 4:06 PM | |
Posts: 8946 Rating: (999) |
Perhaps you also try to reduce "max. waiting time"... |
This contribution was helpful to2 thankful Users |
8/12/2015 4:26 PM | |
Posts: 8946 Rating: (999) |
You are welcome! |