8/22/2019 3:28 PM | |
Joined: 7/9/2015 Last visit: 3/24/2025 Posts: 4207 Rating:
|
Hi, yes you can use S7-Communication with PUT/GET instruction but then you have to project conection with unspecified partner and in your partner PLC you don´t have to do anythin. There is an example with put / get: How do you configure and program an S7 connection and the FB15 "PUT" and FB14 "GET" function blocks for data transfer between an S7-1200 CPU and an S7-300 CPU?Regards, Towome |
|
|
This contribution was helpful to
1 thankful Users |
8/22/2019 4:55 PM | |
Joined: 5/13/2019 Last visit: 3/18/2025 Posts: 34 Rating:
|
I have another CPU 1212C DC/DC/DC and I'm trying to get data from CPU 1214C DC/DC/DC. Like you said I choose the partner unkown. But now I'm getting that error: Illegal parameter assignment for RD_1 I cannot figured out what the problem is. |